See if you have the room capacity to "Roll" the 1" outlet of the 3", up
from horizontal enough,
to use a 1" x 0'-2" to an ell, then nipple over to a 1 x 1/2 ell (or 1"
ell and drop to RC) and install a pendant.
Roll enough so the deflector "just below" the bottom of the 3". That may
make the 22" directive,
have no obstruction to discharge, and keep in close to the 3" main.
May be the best effort to meet the directive.
R. Mark Walker - SET
M. WALKER SPRINKLER CO. Syracuse, NY
On 1/14/2017 7:32 PM, Greg McGahan wrote:
> Travis,
>
> In one of the classes I have taken - I cannot remember when or where -
> the instructor was on the NFPA #13 committee and he implicitly said
> that the verbiage was intended for "nominal" pipe size - not actual
> measurement. I have NOT heard anything since to collaborate this comment.
>
>
>
>
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
>
> On Sat, Jan 14, 2017 at 1:04 PM, Brad Casterline
> <***@gmail.com <mailto:***@gmail.com>> wrote:
>
> It sounds like a good challenge Travis, and congratulations for
> getting the contract-- the self employed designer who turns down
> any work has never lacked for beer and cigarette money.
> And typical of goverment work, there are the doers vs the
> reviewers, and every which way the doers turn they are screwed by
> an inch or two.
> When the Corp of Eng is the AHJ though I have had good luck with
> the field people- they seem to know when you have gotten as close
> to the intent as reality allows-- ie, instead of deflector
> distance they look at 'bulb' distance- within an inch or two, and
> rightly so.
>
> We NICET IVs who can design, calc, bim coordinate, and stocklist
> are often the saviours of projects that would otherwise be a total
> cluster without us.
>
> Brad
>
> On Jan 14, 2017 10:56 AM, "Travis Mack, SET" <***@mfpdesign.com
> <mailto:***@mfpdesign.com>> wrote:
>
> Unfortunately, we do not have the ability to downsize the
> piping. It will be a matter of reworking the existing pipe
> sizing. This consultant took the easy way out and didn't
> really pay attention to many things. The job has over 100 psi
> available. They have 2" branch lines and 3" mains for
> everything. I can not decrease sizing at all. I just have to
> make sure that the new routings I have to do with the pipe
> sizing per their plan is still capable of delivering the
> minimum required densities.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271 <tel:%28480%29%20505-9271>
> fax:866-430-6107 <tel:%28866%29%20430-6107>
> email:***@mfpdesign.com <mailto:email:***@mfpdesign.com>
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> <https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
> Send large files to us via:https://www.hightail.com/u/MFPDesign
> <https://www.hightail.com/u/MFPDesign>
> LinkedIn:https://www.linkedin.com/in/travismack
> <https://www.linkedin.com/in/travismack>
>
> On 1/14/2017 9:46 AM, Brad Casterline wrote:
>>
>> Well said Mr. Mack!
>>
>> Since you will be fixing The Consultant's effort I predict
>> you will resize the branchlines to 2.5", max, so the problem
>> goes away. This should be easy in LH and OH, as you know,
>> because it is a simple matter of a 1" sprig or arm over from
>> a 3" branchline versus an SSU directly on a 2.5" branchline.
>>
>> WBR, 2+2=4 .
>>
>> On Jan 13, 2017 9:26 PM, "Travis Mack, SET"
>> <***@mfpdesign.com <mailto:***@mfpdesign.com>> wrote:
>>
>> Thank you. I think that those of us in this industry
>> (and I believe most are like this) that truly love what
>> we do and view it as a life saving endeavor every day
>> want to always do the best possible thing and fix every
>> problem that is found so that the project goes on with
>> limited hiccups and we all move on to the next project so
>> we can protect more lives.
>>
>> I can pretty much guarantee that I will end up making it
>> meet NFPA 13 critieria, coordinating and re-calculating
>> the project to make sure that at the end of the day,
>> should something happen, the required amount of wet stuff
>> will get on the hot stuff. My customer and their
>> customer can decide how they want to handle the
>> re-submittal and extra time/schedule impact that will
>> possibly happen.
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271 <tel:%28480%29%20505-9271>
>> fax:866-430-6107 <tel:%28866%29%20430-6107>
>> email:***@mfpdesign.com <mailto:email:***@mfpdesign.com>
>>
>> http://www.mfpdesign.com
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> <https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
>> Send large files to us via:https://www.hightail.com/u/MFPDesign
>> <https://www.hightail.com/u/MFPDesign>
>> LinkedIn:https://www.linkedin.com/in/travismack
>> <https://www.linkedin.com/in/travismack>
>>
>> On 1/13/2017 8:12 PM, Ed Kramer wrote:
>>>
>>> Travis,
>>>
>>> As a design professional (and youre a good one), youre
>>> expected to know and abide by the standards. However,
>>> in this case, youre not the designer. Since you have
>>> a contractual connection to this project, Id argue
>>> youre morally (and to a less extent legally) obligated
>>> to notify the company youre contracted with about this
>>> design flaw. Make sure you put it in writing. If the
>>> powers-that-be determine its OK to install directly on
>>> the 3 main, well thats beyond your control.
>>> Notify them (in writing) and sleep well at night.
>>>
>>> But thats just me.
>>>
>>> Ed Kramer
>>>
>>> Bamford Fire Sprinkler
>>>
>>> *From:*Sprinklerforum
>>> [mailto:sprinklerforum-***@lists.firesprinkler.org
>>> <mailto:sprinklerforum-***@lists.firesprinkler.org>]
>>> *On Behalf Of *Travis Mack *Sent:* Friday, January 13,
>>> 2017 5:25 PM *To:*
>>> ***@lists.firesprinkler.org
>>> <mailto:***@lists.firesprinkler.org>
>>> *Subject:* Uprights on 3" pipe
>>>
>>> In a light or ordinary hazard area, would you be able to
>>> justify uprights directly on a 3" main?
>>>
>>> I have been hired to do the 3D coordination of a project
>>> designed by a consultant. The consultant indicated
>>> uprights directly on the 3" main.
>>>
>>> I can justify it in that the main is non-structural and
>>> this is a light hazard area. However, there is also the
>>> section that states you can not put uprights on pipe 3"
>>> and larger without a sprig or arm over that would comply
>>> with the 3x rule.
>>>
>>> There is no room to lower the pipe and I am
>>> semi-restricted from lateral movement for various other
>>> reasons.
>>>
>>> What does the collective wisdom think with this
>>> scenario? And I don't need formulae with a hundred
>>> exponents and variables to figure this out.
>>>
>>> Have a great weekend. Thanks in advance.
>>>
>>> Travis Mack, SET
>>>
>>> MFP Design, LLC
>>>
>>> "Follow" us on Facebook:
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> <https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
>>>
>>> Send large files to MFP Design via:
>>>
>>> https://www.hightail.com/u/MFPDesign
>>> <https://www.hightail.com/u/MFPDesign>
>>>
>>> Sent from my iPhone
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> ***@lists.firesprinkler.org
>>> <mailto:***@lists.firesprinkler.org>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>> _______________________________________________
>> Sprinklerforum mailing list
>> ***@lists.firesprinkler.org
>> <mailto:***@lists.firesprinkler.org>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> ***@lists.firesprinkler.org
>> <mailto:***@lists.firesprinkler.org>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
> _______________________________________________ Sprinklerforum
> mailing list ***@lists.firesprinkler.org
> <mailto:***@lists.firesprinkler.org>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>
>
> _______________________________________________ Sprinklerforum
> mailing list ***@lists.firesprinkler.org
> <mailto:***@lists.firesprinkler.org>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> ***@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org