Stainless Steel pipe in sprinkler systems
Morey, Mike
2015-04-02 13:59:20 UTC
Permalink
I'm sure this has been addressed but I'm not finding it after some searching, are there stainless pipes that fall into the general approvals of NFPA 13 (I don't have full access to ASTM/ANSI but the stuff called out in NFPA 13 doesn't seem to be for stainless pipe), or is there specifically approved stainless pipe/fittings for sprinkler work? Or will we need to get a variance based on it being "better"? We're working in a clean environment and are probably going to provide socket weld fittings or threaded fittings and back weld them (other than the heads obviously). Socket weld fittings are mentioned, but the only mention of stainless anywhere in the standard is the C factor table.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
***@bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=mailto%3amanta%40bmwc.com> | www.bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=http%3a%2f%2fwww.bmwc.com%2f>
Art Tiroly
2015-04-02 15:53:03 UTC
Permalink
The problem may be joining pipe and outlets. What about copper?


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org]
On Behalf Of Morey, Mike
Sent: Thursday, April 02, 2015 9:59 AM
To: ***@lists.firesprinkler.org
Subject: Stainless Steel pipe in sprinkler systems

I'm sure this has been addressed but I'm not finding it after some
searching, are there stainless pipes that fall into the general approvals of
NFPA 13 (I don't have full access to ASTM/ANSI but the stuff called out in
NFPA 13 doesn't seem to be for stainless pipe), or is there specifically
approved stainless pipe/fittings for sprinkler work? Or will we need to get
a variance based on it being "better"? We're working in a clean environment
and are probably going to provide socket weld fittings or threaded fittings
and back weld them (other than the heads obviously). Socket weld fittings
are mentioned, but the only mention of stainless anywhere in the standard is
the C factor table.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
***@bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDt
QSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=mailto%3amanta%40b
mwc.com> |
www.bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQS
kfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=http%3a%2f%2fwww.bmw
c.com%2f>
Morey, Mike
2015-04-02 17:39:26 UTC
Permalink
Typically the cleaning solvents used are not brass/copper friendly. I'm guessing since the request was for stainless pipe the sprinklers will be exposed so they'll be some form of corrosion resistant heads (wax/lead?), I would assume the heads would be soft enough to seal well but I'll have to pass that question on.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
***@bmwc.com | www.bmwc.com

________________________________________
From: Sprinklerforum <sprinklerforum-***@lists.firesprinkler.org> on behalf of Art Tiroly <***@atcofirepro.com>
Sent: Thursday, April 02, 2015 11:53 AM
To: ***@lists.firesprinkler.org
Subject: RE: Stainless Steel pipe in sprinkler systems

The problem may be joining pipe and outlets. What about copper?


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org]
On Behalf Of Morey, Mike
Sent: Thursday, April 02, 2015 9:59 AM
To: ***@lists.firesprinkler.org
Subject: Stainless Steel pipe in sprinkler systems

I'm sure this has been addressed but I'm not finding it after some
searching, are there stainless pipes that fall into the general approvals of
NFPA 13 (I don't have full access to ASTM/ANSI but the stuff called out in
NFPA 13 doesn't seem to be for stainless pipe), or is there specifically
approved stainless pipe/fittings for sprinkler work? Or will we need to get
a variance based on it being "better"? We're working in a clean environment
and are probably going to provide socket weld fittings or threaded fittings
and back weld them (other than the heads obviously). Socket weld fittings
are mentioned, but the only mention of stainless anywhere in the standard is
the C factor table.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
***@bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDt
QSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=mailto%3amanta%40b
mwc.com> |
www.bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQS
kfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=http%3a%2f%2fwww.bmw
c.com%2f>
_______________________________________________
Sprinklerforum mailing list
***@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
John Denhardt
2015-04-02 17:37:32 UTC
Permalink
Viking makes Stainless steel sprinklers.

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of Morey, Mike
Sent: Thursday, April 02, 2015 1:39 PM
To: ***@lists.firesprinkler.org
Subject: Re: Stainless Steel pipe in sprinkler systems

Typically the cleaning solvents used are not brass/copper friendly. I'm guessing since the request was for stainless pipe the sprinklers will be exposed so they'll be some form of corrosion resistant heads (wax/lead?), I would assume the heads would be soft enough to seal well but I'll have to pass that question on.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
***@bmwc.com | www.bmwc.com

________________________________________
From: Sprinklerforum <sprinklerforum-***@lists.firesprinkler.org> on behalf of Art Tiroly <***@atcofirepro.com>
Sent: Thursday, April 02, 2015 11:53 AM
To: ***@lists.firesprinkler.org
Subject: RE: Stainless Steel pipe in sprinkler systems

The problem may be joining pipe and outlets. What about copper?


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org]
On Behalf Of Morey, Mike
Sent: Thursday, April 02, 2015 9:59 AM
To: ***@lists.firesprinkler.org
Subject: Stainless Steel pipe in sprinkler systems

I'm sure this has been addressed but I'm not finding it after some
searching, are there stainless pipes that fall into the general approvals of
NFPA 13 (I don't have full access to ASTM/ANSI but the stuff called out in
NFPA 13 doesn't seem to be for stainless pipe), or is there specifically
approved stainless pipe/fittings for sprinkler work? Or will we need to get
a variance based on it being "better"? We're working in a clean environment
and are probably going to provide socket weld fittings or threaded fittings
and back weld them (other than the heads obviously). Socket weld fittings
are mentioned, but the only mention of stainless anywhere in the standard is
the C factor table.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
***@bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDt
QSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=mailto%3amanta%40b
mwc.com> |
www.bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQS
kfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=http%3a%2f%2fwww.bmw
c.com%2f>
_______________________________________________
Sprinklerforum mailing list
***@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
***@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Thomas Watt
2015-04-03 13:41:52 UTC
Permalink
Why not grooved? Victaulic has SS couplings and mechanical tees.
Just a thought...
b***@comcast.net
2015-04-08 05:12:42 UTC
Permalink
Did they say which stainless would be compatible? 304, 316, ...

Bruce


----- Original Message -----

From: "Mike Morey" <***@bmwc.com>
To: ***@lists.firesprinkler.org
Sent: Thursday, April 2, 2015 6:59:20 AM
Subject: Stainless Steel pipe in sprinkler systems

I'm sure this has been addressed but I'm not finding it after some searching, are there stainless pipes that fall into the general approvals of NFPA 13 (I don't have full access to ASTM/ANSI but the stuff called out in NFPA 13 doesn't seem to be for stainless pipe), or is there specifically approved stainless pipe/fittings for sprinkler work? Or will we need to get a variance based on it being "better"? We're working in a clean environment and are probably going to provide socket weld fittings or threaded fittings and back weld them (other than the heads obviously). Socket weld fittings are mentioned, but the only mention of stainless anywhere in the standard is the C factor table.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
***@bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=mailto%3amanta%40bmwc.com> | www.bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=http%3a%2f%2fwww.bmwc.com%2f>
_______________________________________________
Sprinklerforum mailing list
***@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Loading...