Conveyor equipment in storage occupancies
Steve Leyton
2015-01-05 18:39:01 UTC
Permalink
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in a
panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into the
building but ... it's also possible that I'm getting paranoid in my
mid-life crisis.



Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this application
that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...



Happy New Year everybody!



Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 210

San Diego, CA 92108

-------------------------------------------

Ph: 619.255.8964 - ext. 102

Fax: 619.255.9364

Cell: 619.972.5696
Todd - Work
2015-01-05 19:38:01 UTC
Permalink
Steve,

Not sure of your storage arrangement or how the conveyors fit in with it. I just finished a single stream recycling facility with 100+ sprinklers under conveyors in a 28000 sqft building. I ended up following standard obstruction rules and it worked out reasonably well. It was pretty much impossible to show on a plan, so I did my best on that and worked with the contractor on where and how once the structure was up.

Todd

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
Post by Steve Leyton
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in a
panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into the
building but ... it's also possible that I'm getting paranoid in my
mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this application
that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Matt Grise
2015-01-05 20:08:45 UTC
Permalink
I have seen these handled a couple of ways:

1 - if the conveyors are low to the ground (2-4' aff), I have seen them allowed to be excluded as long as there are barriers (or lines on the floor) to prevent storage or accumulation of combustible underneath. That would be like the final roll-out conveyor for a pick-n-pack setup where the boxes are rolling towards a palletizing/truck loading area and the conveyor is not within racking - the ESFR system is basically giving OH level protection.

2 - The most common arrangement I have seen is to route a line of standard spray heads under the conveyor calc'd for oh2 with the thought that any pile of combustibles that found its way under the conveyor would be less than 12' tall.

3 - sometimes if the conveyors are high up or if they cross the storage areas they get a line of ESFR's under them since there could be a high hazard fire under them.

When the pipe is under the conveyors it is usually hung from the framing - either along the sides or down the middle - wherever is easier for routing. (I also don't have to worry about seismic concerns so I am not sure how the bracing might play into that)

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO
 
913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com
 

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Monday, January 05, 2015 1:38 PM
To: ***@lists.firesprinkler.org
Subject: Re: Conveyor equipment in storage occupancies

Steve,

Not sure of your storage arrangement or how the conveyors fit in with it. I just finished a single stream recycling facility with 100+ sprinklers under conveyors in a 28000 sqft building. I ended up following standard obstruction rules and it worked out reasonably well. It was pretty much impossible to show on a plan, so I did my best on that and worked with the contractor on where and how once the structure was up.

Todd

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
Post by Steve Leyton
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in
a panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into
the building but ... it's also possible that I'm getting paranoid in
my mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this
application that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
Roland Huggins
2015-01-05 20:13:08 UTC
Permalink
The challenge comes when there is a metal grate walkway with it (or worse yet just a walkway). You’re suppose to use an intermediate sprinkler beneath metal grating and use the same sprinkler type as the ceiling beneath obstructions. Still looking for an ESFR intermediate.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
Post by Steve Leyton
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in a
panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into the
building but ... it's also possible that I'm getting paranoid in my
mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this application
that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Scott A Futrell
2015-01-05 20:28:06 UTC
Permalink
I'd add that there are several 'trap doors' Steve. What is being conveyed?
Do the conveyors need to be interlocked on sprinkler activation?
How wide are they?
Are there multiple levels/layers?
What is going on below the conveyors (process, fuel load, nothing, and so on)?
More...

Scott
 
Office: (763) 425-1001x12
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of Roland Huggins
Sent: Monday, January 05, 2015 2:13 PM
To: ***@lists.firesprinkler.org
Subject: Re: Conveyor equipment in storage occupancies

The challenge comes when there is a metal grate walkway with it (or worse yet just a walkway). You’re suppose to use an intermediate sprinkler beneath metal grating and use the same sprinkler type as the ceiling beneath obstructions. Still looking for an ESFR intermediate.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
Post by Steve Leyton
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in
a panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into
the building but ... it's also possible that I'm getting paranoid in
my mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this
application that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
***@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
rongreenman .
2015-01-05 22:37:39 UTC
Permalink
I think this one needs a lot of banter (defining the problem six different
ways, ideas, sketches, why certain ideas won't work, why could work, blah,
blah, blah.) Lot's of fortified coffee. Oh–––and client dollars.
Post by Scott A Futrell
I'd add that there are several 'trap doors' Steve. What is being conveyed?
Do the conveyors need to be interlocked on sprinkler activation?
How wide are they?
Are there multiple levels/layers?
What is going on below the conveyors (process, fuel load, nothing, and so on)?
More...
Scott
Office: (763) 425-1001x12
Cell: (612) 759-5556
-----Original Message-----
Huggins
Sent: Monday, January 05, 2015 2:13 PM
Subject: Re: Conveyor equipment in storage occupancies
The challenge comes when there is a metal grate walkway with it (or worse
yet just a walkway). You’re suppose to use an intermediate sprinkler
beneath metal grating and use the same sprinkler type as the ceiling
beneath obstructions. Still looking for an ESFR intermediate.
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
Post by Steve Leyton
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in
a panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into
the building but ... it's also possible that I'm getting paranoid in
my mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this
application that I might want to know about before taking a meeting with
the client
Post by Steve Leyton
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

***@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
Steve Leyton
2015-01-05 20:21:20 UTC
Permalink
I'm prepared to pitch that ESFR isn't required at the ceiling because there's not any storage below the equipment, just handling and debris. So it's a convenience only to leave the ESFR at the roof ...

SL





-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of Roland Huggins
Sent: Monday, January 05, 2015 12:13 PM
To: ***@lists.firesprinkler.org
Subject: Re: Conveyor equipment in storage occupancies

The challenge comes when there is a metal grate walkway with it (or worse yet just a walkway). You’re suppose to use an intermediate sprinkler beneath metal grating and use the same sprinkler type as the ceiling beneath obstructions. Still looking for an ESFR intermediate.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
Post by Steve Leyton
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in
a panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into
the building but ... it's also possible that I'm getting paranoid in
my mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this
application that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
***@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
R***@aerofire.com
2015-01-05 21:15:01 UTC
Permalink
What edition of 13 are you using?

Ron fletcher Sent from my iPhone
Post by Steve Leyton
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in a
panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into the
building but ... it's also possible that I'm getting paranoid in my
mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this application
that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Steve Leyton
2015-01-05 23:07:24 UTC
Permalink
2013.

I'm already familiar with 8.12 ...

SL


-----Original Message-----
From: Sprinklerforum
[mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of
***@aerofire.com
Sent: Monday, January 05, 2015 1:15 PM
To: ***@lists.firesprinkler.org
Subject: Re: Conveyor equipment in storage occupancies

What edition of 13 are you using?

Ron fletcher Sent from my iPhone
Post by Steve Leyton
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never
occupied)
Post by Steve Leyton
building is furnished throughout with ESFR. There are no
complications
Post by Steve Leyton
and I get the report approved and ... the client just contacted me in
a panic asking for a new report or an addendum to the previous one
that
Post by Steve Leyton
addresses their conveyor equipment. That they somehow NEVER
mentioned
Post by Steve Leyton
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into
the building but ... it's also possible that I'm getting paranoid in
my mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this
application that I might want to know about before taking a meeting
with the client
Post by Steve Leyton
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me
anything of substance regarding connection points for sprinkler piping
under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
C***@ch2m.com
2015-01-05 21:20:47 UTC
Permalink
Is the belting FM approved non-combustible? What is the width?

Does the conveyor pass through any rated walls or separated occupancies?

What is driving you to think you have to provide sprinklers below?

Where is the conveyor installed, just above floor level, overhead, etc?

Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
***@ch2m.com


-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of Steve Leyton
Sent: Monday, January 05, 2015 1:39 PM
To: ***@firesprinkler.org
Subject: Conveyor equipment in storage occupancies

So ... I get hired to write a tech report on an S-1 occupancy and it's pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in a panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into the building but ... it's also possible that I'm getting paranoid in my mid-life crisis.



Anyway, besides the obvious regarding obstructions as they pertain to ESFR, can anyone tell me if there are any trap doors in this application that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me anything of substance regarding connection points for sprinkler piping under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...



Happy New Year everybody!



Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 210

San Diego, CA 92108

-------------------------------------------

Ph: 619.255.8964 - ext. 102

Fax: 619.255.9364

Cell: 619.972.5696
Steve Leyton
2015-01-05 23:14:49 UTC
Permalink
Belts occur at different elevations and complements of single-level, two- and three- levels high. Assuming protection below because existing ESFR will be obstructed and AHJ is notoriously strict. No rated walls, don't know yet about composition of belts.

SL



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of ***@ch2m.com
Sent: Monday, January 05, 2015 1:21 PM
To: ***@lists.firesprinkler.org
Subject: RE: Conveyor equipment in storage occupancies

Is the belting FM approved non-combustible? What is the width?

Does the conveyor pass through any rated walls or separated occupancies?

What is driving you to think you have to provide sprinklers below?

Where is the conveyor installed, just above floor level, overhead, etc?

Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
***@ch2m.com


-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of Steve Leyton
Sent: Monday, January 05, 2015 1:39 PM
To: ***@firesprinkler.org
Subject: Conveyor equipment in storage occupancies

So ... I get hired to write a tech report on an S-1 occupancy and it's pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in a panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into the building but ... it's also possible that I'm getting paranoid in my mid-life crisis.



Anyway, besides the obvious regarding obstructions as they pertain to ESFR, can anyone tell me if there are any trap doors in this application that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me anything of substance regarding connection points for sprinkler piping under the widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...



Happy New Year everybody!



Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 210

San Diego, CA 92108

-------------------------------------------

Ph: 619.255.8964 - ext. 102

Fax: 619.255.9364

Cell: 619.972.5696







_______________________________________________
Sprinklerforum mailing list
***@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Ed Cyr
2015-01-06 16:48:22 UTC
Permalink
Steve,
You may want to check out FM Global Data Sheet 7-11. It contains a very
comprehensive overview of conveyors and required protection.

Ed Cyr
Post by Steve Leyton
Belts occur at different elevations and complements of single-level, two-
and three- levels high. Assuming protection below because existing ESFR
will be obstructed and AHJ is notoriously strict. No rated walls, don't
know yet about composition of belts.
SL
-----Original Message-----
Sent: Monday, January 05, 2015 1:21 PM
Subject: RE: Conveyor equipment in storage occupancies
Is the belting FM approved non-combustible? What is the width?
Does the conveyor pass through any rated walls or separated occupancies?
What is driving you to think you have to provide sprinklers below?
Where is the conveyor installed, just above floor level, overhead, etc?
Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC 29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
-----Original Message-----
Sent: Monday, January 05, 2015 1:39 PM
Subject: Conveyor equipment in storage occupancies
So ... I get hired to write a tech report on an S-1 occupancy and it's
pretty straightforward since the existing (brand new and never occupied)
building is furnished throughout with ESFR. There are no complications
and I get the report approved and ... the client just contacted me in a
panic asking for a new report or an addendum to the previous one that
addresses their conveyor equipment. That they somehow NEVER mentioned
or showed on any of the plans that I was given for reference. I have
a nagging suspicion that they may have been trying to sneak it into the
building but ... it's also possible that I'm getting paranoid in my
mid-life crisis.
Anyway, besides the obvious regarding obstructions as they pertain to
ESFR, can anyone tell me if there are any trap doors in this application
that I might want to know about before taking a meeting with the client
and the fire official? I came away from a brief telecon with the
vendor for the equipment a bit concerned, as he couldn't offer me anything
of substance regarding connection points for sprinkler piping under the
widest belts and platforms (he's checking and will get back to
me). In all these years I've never fire protected a system like this;
have done rollers, push-backs, luggage handling systems at two major
airports, dry cleaning handling systems, rotating retail clothing
fixtures, etc., etc. but not a storage conveyor. Just want to be sure
there's no ticking IED's that I haven't accounted for ...
Happy New Year everybody!
Steve Leyton
PROTECTION DESIGN & CONSULTING
2851 Camino del Rio South, Suite 210
San Diego, CA 92108
-------------------------------------------
Ph: 619.255.8964 - ext. 102
Fax: 619.255.9364
Cell: 619.972.5696
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Loading...