Thanks Bruce. You are right, and the question was about the maintaining volume water for fire while the same tank is for process or domestic water.
In other cases we put the suction of domestic services water above of the volume for fire service but in this case, we will use the same pipe to feed fire service and domestic water
| | ____________________________________________TO FIRE SERVICE
| | | | |
| | FIRE P. DOMESTIC WATER P. |_______TO DOMESTIC WATER SERVICE
| | | |
|______|-------------------------------------
PROBLEMS:
AVOID TO DOMESTIC WATER SERVICE EMPTY THE FIRE P. CAPACITY VOLUMEN
PRESSURES OF PUMPS, IF DOM. PUMP IS HIGER THAN FIRE PUMPS IT WORKS AS JOCKEY, BUT WITH HIGH FLOW, IT COULD NOT RUN THE FIRE DIESEL PUMP BECAUSE THE SAME BOOSTER PUMP COULD HAND THE FLOW FOR FIRE BUT THE BOOSTER IS NOT A APPROVE EQUIPMENT FOR THIS USE.
De: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] En nombre de Bruce Verhei
Enviado el: jueves, 8 de diciembre de 2016 04:57 p. m.
Para: ***@lists.firesprinkler.org
Asunto: Re: WATER STORAGE TANK AND PUMPS ARRANGEMENT FOR FIRE AND SERVICE WATER
Cesar,
If you are specifically working with FM to establish a Highly Protected Risk property it is best that you contact their project representative directly. They will put you in contact with their fire protection engineer.
Or is FM instead being used as an available set of standards?
Is your question how to account for water volume in normal sanitary and industrial use, while maintaining adequate reserve for fire sprinkler systems?
Best
Bruce Verhei
On Dec 8, 2016, at 15:37, Cesar Lira < <mailto:***@demek.com> ***@demek.com> wrote:
I have a Question.
We need to install a water storage tank, and pumps for a industrial park, this industrial park has a 20 buildings feed with a single 12 inches diameter pipe. It has two branches for every building one for fire sprinklers connection and another one for services water.
In pumps room we will to have storage tank volume for both systems, and diesel, electric and booster pumps.
There is any rule for this pumps arrangement according to FM requirements?, to avoid service or process systems use the part of water of the fire protection.
Thanks.
CLR
_____
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
El software de antivirus Avast ha analizado este correo electrónico en busca de virus.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> www.avast.com
_______________________________________________
Sprinklerforum mailing list
<mailto:***@lists.firesprinkler.org> ***@lists.firesprinkler.org
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
---