We always split the systems where the K factor changes. However, if the addition is small the total area is under 40k sqft you would probably have to change all the heads on that system to K17.
Ron F
-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org] On Behalf Of James Crawford
Sent: Thursday, March 19, 2015 11:21 AM
To: ***@lists.firesprinkler.org
Subject: RE: ESFR Sprinkler Heads
Thanks Roland
The AHJ has impose a greater reduction and if I use the new pressures the existing system is 3 psi short.
My concern with using two different K factor heads is the overlap area where two different pressures would be required causing over discharge on the K17 heads.
Thank you
James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email ***@phaserfire.ca
-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-***@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Thursday, March 19, 2015 11:05 AM
To: ***@lists.firesprinkler.org
Subject: Re: ESFR Sprinkler Heads
you can have multiple design basis covering different portions of a building. They could present different K-factors or types of sprinklers.
There are explicit requirements that address the interface between them.
What do you mean the AHJ has dropped the pressure? Does that mean the water purveyor has dropped the pressure to the area or that the AHJ has imposed a greater reduction on the actual supply as a safety factor. In other words, is the existing system still providing adequate protection (not an issue for imposed reductions) ?
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
Post by James CrawfordWe are doing an addition to an existing warehouse, the existing
warehouse is protected with ESFR K14 uprights, since the building was
constructed the AHJ has dropped the water pressures in the area by 10 psi.
Due to the pressure drop I cannot use the K14 heads for the addition,
can you mix ESFR sprinkler heads in the same warehouse area, I would
need K17 heads for the addition, The addition would be open to the
existing warehouse space. Or do I need to change all the heads in the
existing warehouse to match?
Thank you
James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Fax 604-888-4732
Cel 604-790-0938
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
***@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org