Post by S***@aerofire.comThank you Richard and Brad.
These are some of the exact points I was looking at/for. Up to this point
we had only used them under garage doors. But like Duane brought up, we
were wondering if they can be installed under garage doors and be expected
to operate, then shouldn't they also be allowed to be installed in
"exposed" scenarios. Maybe this just one of those "calculated risks" by
the committee if no other testing has been done.
Moving on, so if I follow 8.7.4.1.2.2, and located the deflector
accordingly off the "wall". What are the other defining characteristics of
this "wall"? How deep is it? How long does it have to be? As far as I
know "wall" isn't defined in Chapter 3. You may laugh and think I am going
too far with this, but one of the major sprinkler manufactures states the
following in one of their product listings "Horizontal sidewall sprinklers
are designed for installation along a wall or the side of a beam". Since
they are clearly indicating beams are acceptable for proper operation, can
I assume "wall" in 8.7.4.1.2.2 doesn't mean it has to run from floor to
ceiling. From this point going forward I can see someone arguing from (6)
different routes, some of which could be considered "educated guesses".
First (2) should be completely acceptable but not preferred, Next (3) have
their pros/cons and varying degrees of applicability, last (1) is the most
preferred but probably won't be
accepted.
(1) Build a wall.
(2) Install a beam.
(3) Use the definition of Compartment from 3.3.6. A sidewall can be
installed in a "compartment", so an 8" lintel should be sufficient. Since
the 8" lintel allows a maximum opening of 8ft in the wall, space the heads
every 8ft and run the lintel the length of the sidewalls.
(4) Use the definition of Draft Curtain from 8.4.6.4.1. Since this is
acceptable to separate sprinklers with different response times, it will
clearly delay the heat travel long enough for a sprinkler to operate. This
would require a barrier 2ft deep running the length of the sprinklers. No
apparent restriction on sprinkler spacing.
(5) Use the definition of Draft Stop from 8.15.4.2. Since this is
acceptable to delay heat traveling vertically from floor to floor. This
would require a barrier 18in deep with heads spaced 6ft apart.
(6) If we decide the wall/beam isn't required to be a heat trap, but
rather a protection of spray from other sprinklers. Use the definition for
Baffles with Sidewalls 8.7.3.4. Baffles are at least 8" long, 6" high, be
between 2in and 3in above the deflector, and the bottom be at least even
with the deflector.
Obviously I would like to choose (6) if acceptable. However do you see
any viability of these (4) "educated guesses"?
I appreciate any further input/opinion and of course your time to listen to me ramble on.
Thanks,
Sean VG
-----Original Message-----
Casterline
Sent: Tuesday, December 22, 2015 9:58 AM
Subject: RE: can sidewalls be installed when not located next to a wall?
*****
Can a horizontal sidewall sprinkler be installed in the center of a room
(flat, smooth clg) provided sprinkler coverage is added behind the
sidewall? In other words, not installed near a wall or soffit.
In reality a sidewall installed 4" to 6" below the ceiling (away from a
wall/soffit) should activate in similar fashion as exposed pendents and
uprights (1" - 12" below clg). If code permits "exposed" sidewalls to be
installed below roll up doors without soffits, can't an "exposed"
sidewall be installed elsewhere?
Is there anything in the listing of a sidewall that requires the sprinkler
be installed on a wall or soffit? Are there any ROP/ROC responses from the
committee that would help answer the question?
Thoughts?
Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research
Services National Institutes of Health
301-496-0487
Duane,
NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and horizontal
sidewalls in relation to the wall that they are projected from.
Sidewall sprinklers cannot be positioned in the center of a room as a pendant.
Dale F. Wingard, SET
Design Manager
Triple "A" Fire Protection, Inc.
251.649.2034
********
Brad
-----Original Message-----
On Behalf Of Richard Carr
Sent: Tuesday, December 22, 2015 10:19 AM
Subject: RE: can sidewalls be installed when not located next to a wall?
Under overhead doors is only place I know is acceptable without a wall.
Sent from my T-Mobile 4G LTE Device
-------- Original message --------
Date: 12/22/2015 11:14 AM (GMT-05:00)
Subject: can sidewalls be installed when not located next to a wall?
Hi All,
I can't check the forum archives right now because the website isn't
loading for me for some reason. Based on NFPA 13 2013.
Can sidewalls be installed when not located next to a wall?
Assuming we meet the all the minimum/maximum spacing requirements,
vertical distance below the deck requirements, standard spray sprinklers,
ordinary hazard occupancy, noncombustible construction. Walking from
branchline to branchline left to right, can I install upright, upright,
sidewall facing right, sidewall facing left, upright, upright. With
spacing from upright to upright equal to 12ft, spacing from upright to
backside of sidewall of 6ft, and spacing from sidewall face to sidewall
face equal to 20ft. Is this acceptable?
The first thing most people say is "will the sidewall be next to something
like a baffle or installed with the pipe in a soffit?" As of now, no,
there is nothing behind the sidewalls. If something is required, please
help me find the direction in the code for this requirement and design
parameters.
Because right now all I am finding is a lot of "grey" area that people can
interpret whichever way suits their needs. I'm looking for "black and
white" if it is in there. If it's only "grey", opinions are greatly
appreciated.
Thank you for your time and help!
Thanks,
Sean VG
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org